I thought I had got everything set up to avoid the Victron MPPT RS capacitors and the Victron Quattro capacitors from demanding a massive in rush from my "battery bank." I bought a light bulb to use as a resistor and used a separate 48V battery bank to pre-charge my capacitors in the MPPT RS before I turned on my 38KW of 8 Pylontech US5000 batteries. That worked, no alarm from the Pylontech when they were switched on.
But once I wired up the Quattro, it took forever for the light bulb to dim as the current filled up both the Quattro and MPPT capacitors and although the bulb did go dim, when I switched on my Pylontech batteries I got an alarm on the first of eight batteries. That alarm quickly went out and everything was fine.
Then, I did some wiring so I turned off the Cerbo GX (I put a toggle switch on the wire to flip it on and off to keep it from robbing the capacitors on the system) and I turned off the MPPT and the Quattro. Did my wiring and figured I didn't need to pre-charge the caps since they should be full after running for several days in a row. But nope, flipped on my Pylontech and got an alarm again.
How are we supposed to deal with all this Victron equipment connected to a bus bar with caps that apparently are insatiable and don't stay charged? I hate seeing the alarm on my expensive batteries every time I need to make a change.
How do others handle this?