I have a Quattro and I'm looking to turn on line 2 while inverting… Presently only line one gets power from the inverter… I realize that the phase shift requires time but line 2 doesn't come on while inverting.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a Quattro and I'm looking to turn on line 2 while inverting… Presently only line one gets power from the inverter… I realize that the phase shift requires time but line 2 doesn't come on while inverting.
With the default configuration AC Out 2 is only active while the grid is connected.
But you can overwrite that behavior with the "programmable relay" assistant (you need two; one for ON and one for OFF).
https://www.victronenergy.com/live/assistants:start