Hi All,
Background
I have been running a single Multiplus-II 48/5000 (HQ2203) for the last 12months with ESS enabled, and its been working great. Charges overnight, and during the day it keeps grid usage close to 0 Watts.
I purchased a 2nd Multiplus-II 48/5000 (HQ2237) earlier this year, and finally connected it last week.
The units were installed with same length cables (Both AC & DC), and the units have been configured as Parallel using QuickConfigure. Both have the same settings and ESS Assistant applied.
The Probem
ESS is unable to reach the SetPoint (0 Watts).
The CerboGX shows that when AC-OUT (The House) is consuming 500W, ESS seems to discharge too much from the battery and therefore exports 150W - to the grid.
This figure drifts further when the load increases.
Thoughts
- Could the build dates of my Multiplus-II's be incompatible?
- Is the 1.2Meter x 10mm2 cable too low resistance?
- I used the same cable on AC-IN and AC-OUT
- Is the 0.6Meter x 50mm2 DC Cabling too large?
I have searched the forum and found a couple of similar posts, but most do not have solutions to this issue.
- Grid Setpoint not tracking very well when running Parallel Multiplus - Victron Community (victronenergy.com)
- Parallel Multiplus II problem while AC IN is connected - Victron Community (victronenergy.com)
- @sgrigor1 @Michelle Konzack - Perhaps you'd consider commenting on my post?
- Does your post suggest that you are using 4mm2 cable for your AC-IN & AC-OUT?
I understand the idea on adding some resistance, but what about Max Current of that cable?