Phoenix MultiPlus charger input frequency

I have a Victron Phoenix Multi Plus 24/3000/70 charger/inverter on my European boat which was installed in France around 2009. The data sheet states that the charger only has an input frequency range of between 45-55hz. However the manual also states that the product can operate at 50hz or 60hz. Can anyone please confirm if the charger will work ok if i plug it into a shore supply in the US of 220v at 60hz? I don't mind if it passes through 60hz but i want to be sure that it wont blow up the charger.

chargerfrequency
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

According to the manual that I could find, it's adjustable 45-65Hz, 45-55Hz, 55-65Hz. Does your Multi have VE.Bus?

See page 19 of this manual which is the closest to your Multi's model year. Manual is 2007.
https://www.victronenergy.com/upload/documents/Manual%20-%20MultiPlus%203k%20230V%20Ve.Bus%20enabled%20-%20rev%2000%20-%20EN%20NL.pdf

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

syhera avatar image syhera commented ·

Thanks for this. I have the manual for my Multi and it has this description in the manual.

0 Likes 0 ·