I enabled the new solar/wind priority and it does seem to be working correctly. Example - shore power off, AC load 1496W, solar 1100W. Battery 100%. 56.7V. Turn on shore power and input on shore power goes to 1755W. While the PV starts at 1100W it then tapers down to 0W and power from shore power is supplying both charging that AC loads.
Other settings. Dual Quatro, Split Phase, 48V Lithium. Quatro chargers absorb 56.5V, Float 54V. MPPT controllers Absorb 56.5V, Float 55V.
Advanced tab for both Quatros Solar/Wind Priority turned on with 54V.
Is there some relationship between the absorb/float and voltage of the Advanced Setting?
Reviewing the available videos the behavior should be that the PV stays consttant and the shore power would slowly taper down to 0V as the battery is charged through the absorbtion phase to the Sustain phase, assuming that the load is smaller than the PV output.
Thanks in advance.