Setup
100/20 MPPT Victron CC.
Four 250 W Solar used Canadian Panels. all clean tested at 33v / panel out of poss 38V.
Panels wired in series / parallel so not to exceed amps
3 Odyssey 12V AGMs in series
Question/Concern
I'm only getting 275W at peak sun with clean panels,
Following a post by snoobler, https://community.victronenergy.com/questions/111676/getting-very-low-watts-from-charge-controller.html?childToView=111685#comment-111685
would like to just confirm if my CC is limited on charging power coming in based on amp x current battery voltage?
so if current battery voltage is 13, then 13*20 = 260W would be the max allowable power through this CC?
I have an additional 100/20 MPPT Victron CC, 3 AGMs and 4 panels. Is one solution to set up a facsimile and simply distribute the load or is there a different / better alternative?
2nd question:
Also, I spoke with battery tech support at Enersys regarding my Odyssey 12V AGM31 and he had me set the low cutoff at 11.1, suggesting these deep cell batteries like to be discharged to low levels. from what I'm reading on this forum, the cutoff should be like 12.05 or higher??
thanks for the help here.