Hello, I managed to get my multiplus II to a state where it takes priority energy from the grid and not from the battery.
ESS is not working properly. As if the ESS remained in external control.
I was doing read and write over Modbus TCP using LOXONE. I don't know at which step it went wrong.
I made entries in the registers 2704, 2705, 2706, 2901, 37. I wanted to create an energy management system for controlling energy flows according to consumption of appliances using loxone.
I later found out that the Multiplus draws energy from the mains as a priority and not from the battery.
I wanted to return the system to its original state - I canceled the Modbus TCP communication so that Loxone does not interfere with the ESS - no change.
I removed ESS from the system, downloaded a new one from the web, configured it for cooperation with the grid (europa), uploaded it to the system - no change.
I changed the firmware in Gerba - no change.
The load runs from the grid, the PV only charges the batteries. The Grid setpoint parameter does not react to the change.
I managed to achieve the desired state only by cyclically writing the value 0 to register 2706 (every second).
That is not the solution.
I can't help myself anymore.
System: MULTIPLUS-II 48/5000/70-50 (firmware 502, VE.bus version 2623502), SmartSolar MPPT VE.Can 250/85 rev2 (firmware v3.13), Gerbo GX (firmware v3.10). Battery 48V 225Ah (GEL/AGM type, without BMS).
Could someone advise me on what to do next?
Nero
sorry, the text was translated by Google translator