Good day,
I have a Hatz Diesel 1,9kW 28V 68A which i have setup to 32V because of the voltage drop since it is installed in a distance of 11m to the busbar using H01N2-D 70mm2.
However, when I had an 6kVA Kohler, it was workibg fine together with the MultiPlus-2 24/5000 but with the Hatz it does not work.
Here a short describtion how it should work:
1) MultiPlus-2 close relais for Remote Start of Generator
2) Main Relais 100A connect power to Generator (hsd to be done this way, because the electronic suck 15W in stand-by)
3) electomagnetic fuel valve open
4) Generstor get signal to start
4.1) If the Genetator does not start in 10 seconds diengage Generator
4,2) wait for 1min to cool down the starter
4.3) go back to 4) and try it in total 3 times
4.4) after 4 failed starts, disengage Main Relais and lock it
5) Generator is running until the 248l tank is empty or MultiPlus-2 disengage the RemotevControl
However, this is working manually (I can start/stop the generator even manually with a switch installed in 60m distance in my house) but the MultiPlus-2 does not detect, that something is charging e.G. Voltage increase from 22,2V to 23,8V...
Does someone use a similar setup and got the RemoteControl running with a DC Generator?
Note: currently i have no SmartShunt in the Power Line of the Generator.