Multiplus II 48/3000 PMP482305000 and PMP482305010 parallel compatibility.

Hello all!,


I was wondering if it is possible to run in parallel the diferent hardware revisions of the Multiplus II 48/3000 PMP482305000 and PMP482305010.

Also I would like to know if PMP482305000, the older one still in production and comercially available.

Best regards.

Multiplus-IIbattery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Alfredo,

No, it is not possible to run these two different hardware revisions together in multiphase or parallel systems.

The PMP482305000 is no longer in production, and is no longer being sent to distributors by Victron.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alfredo avatar image alfredo commented ·

Thanks for your answer Guy. Let me one more question... what about the classic line of multiplus? Are them planned to still in production in medium or long term?

Best regards.

0 Likes 0 ·
Show more comments
esterne avatar image esterne commented ·

This is a very bad move from Victron.

Any existing site upgradeability has just been cut off. ( Ie can't add any further Multi's in parallel ).

What is Victron's plan, when you need to replace a faulty unit ( Multiplus II pmp482305000 ) in a site where there are a couple of units running in parallel and or on multiple phases ???

The only option I see is that Victron is going to have to release a firmware that may limit the functionality of the pmp482305010, so that it would be compatible to pmp482305000 in existing sites ?

Or is there something I'm missing ?

0 Likes 0 ·