Armel Peel asked

Using a Quattro inverter with a DC genset

Ahoy!

I couldnt find the answer on the internet, but I am looking at a 58" Hattaras boat that comes with a 20 Northern Lights 20KW generator. I wanted to get a Quattro inverter for both shore power AND generator power, but how would I hook a DC generator up in this situation? The Quattro has dual AC inputs, but would the DC generator have to be connected a different way like directly to the batteries? Would the Orion-TR work for something like that or is that just for the alternator? I found something here labeled Quattro and DC genset

https://www.victronenergy.com/upload/documents/10-QUATTRO-and-DC-genset.pdf

But I am not sure this is exactly what I am looking for. Quite a few extra connections in there and dual inverters.

Thanks for any help guys.


dc system
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·
@Armel Peel

Are you sure it's a DC generator? 20kW is a lot of DC and would be a most unusual choice.

0 Likes 0 ·
Show more comments
1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

If you wanted a DC generator, then the hook up would be as the pdf link mentioned above. Bigest problem with DC generators, is that if you want to charg lithium batteries then you need to regulate the current.