Can 2 multiplus inverters be installed in parallel completely indipendant but feeding the same db? The main reasoning is to improve redundancy. Is there any possible software or electrical issues that may arise?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can 2 multiplus inverters be installed in parallel completely indipendant but feeding the same db? The main reasoning is to improve redundancy. Is there any possible software or electrical issues that may arise?
They have to be connected and configured to run synchronized together.
Connecting them together unsynchronized will cause problems and/or damage.
No. It will end in tears. You could run as independent phases but would have to split your db.
This doc and its rules exist for a reason:
https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems