question

mose avatar image
mose asked

ESS not balancing grid setpoint on load limit

I recently installed a three phase setup with three MultiPlus-II 48/3000/35 (fw 459) with four Pylontech US3000 battery modules.

Everything works. During normal loads ESS balances the grid setpoint and optimizes for self-consumption just fine. Now I discovered an unexpected behaviour regarding what happens when one of the Multis reaches it's load limit during grid connected inverter mode while the other two are not doing much at all.

What I expected:
When one Multi reaches it's load limit additional power is taken from the grid. ESS balances to the configured grid setpoint as the other two are able to provide additional energy.

What happens:
One Multi reaches it's load limit at 3000VA. Additional power is taken from the grid. The other two Multis are only providing their (very small) loads. Power is taken from the grid without balancing to the grid setpoint - energy is bought from the grid altought it could be taken from the battery.

My batteries can provide around 7000VA easily so this can not be the problem. Also the system balances out during normal operation just fine. Is this expected behaviour for ESS? If so, why? Makes no sense to me.

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @mose


I've checked back-stage, and improving this behavior is on the 'todo' list, it might take a while to make this work and test though.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mose avatar image mose commented ·

Okay, so atm this is expected and will BE changed in the future. Will this require a firmware update to the Multis or only CCGX? Could you please inform me when this gets fixed?


From idle curriosity - being also an IT-Professional- how comes that balancing behaves differently in regards to load limit? Would expect that it should be handled the same softwarewise...?

0 Likes 0 ·
mose avatar image mose mose commented ·

@Daniël Boekel (Victron Energy Staff) did you see my comment? Today I noticed in the Changelogs that VE.Bus xxxx460 had "A lot of under the hood changes". Which device does need this improvement the CCGX or the Multi?

0 Likes 0 ·
Show more comments
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @mose
Did you select 'phase compensation' in the settings?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mose avatar image mose commented ·

Yes, Phase compensation in ESS is on.