Inverter turns off after disconnecting shore power

Multiplus 2...

After 2 days of shore power, I disconnected and Inverter wont come on.

When I reconnect shore power, power flows thru but cerbo shows no AC input.

Any ideas appreciated.

Thanks


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
seb71 avatar image
seb71 answered ·

Start by measuring battery voltage and checking battery wires, fuses, switches, etc.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tdentel avatar image
tdentel answered ·

Thanks for your response.

I have 14.5 v from the batts thru the fuse and disconnect to the inverter.