toweri asked

Small generator goes "Overload" EasySolar 24/1600/40 and MPPT 100/50

I attempted to use my small generator (700 W, Inverter output) as additional power source / battery charger on EasySolar 24/1600/40 and MPPT 100/50. This is a 240 volt, off-grid cabin setup.
After a few seconds of running, the generator indicated "Overload" and turned off.
What is the minimum required power of a generator connected to this EasySolar?
Is there an adjustment to reduce required generator power so that a 700 W generator can be used without overloading it?

GeneratorEasySolar All-in-One
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
@Toweri Lower your input voltage limit to about 2.9a (the multi can go down to 2.4a) and reduce your charge current to 20a.

That should lower the load on the genset to about 650w (va?).


0 Likes 0 ·
Show more comments
1 Answer
seb71 avatar image
seb71 answered ·

Take a look at this:

MultiPlus Generator FAQ
https://www.victronenergy.com/live/multiplus_faq