Energy Meter ET112 Not seen by Cerbo GX

Hi I am working my way through a fresh system install. I have a CebroGX with V3 firmware and I am trying to install and configure a ET112 Energy Meter.

The Meter is installed in my consumer unit (by my electrician) with a LAN cable that is about 6m long (the distance to my solar utility room the CebroGX resides).

I have connected the ET112 as per the Victron wiring diagram to ports 4,5, and 6 on the ET112 then to a USB converter I purchased from my Victron Supplier to Orange, Yellow and Black.

20230813-154731.jpg

When I attach the USB converter to the middle USB port on the CebroGX I get a short RX/TX light flash then nothing.


cerbogx-devicelist.jpg


cebrogx-services-energymeters.jpg


ET112 software I spotted another port where a user downloaded the software from the Manufacture of the ET112 device itself. so I did the same.


That see the ET112 no issues at all, so I know the cable connections and the device itself are fine.


et112-meter1.jpg


et112-meter2.jpg


The Address of 30 is a change I made to see if the ET112 was set to a default address of 1 that may have been clashing with other Victron devices. But still no go.

Anyone have any ideas why the CebroGX is refusing to see the ET112 that is clearly working?


Kind regards


Duncan



.

Energy Meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
matt1309 avatar image
matt1309 answered ·

Hi @Duncan.Gardiner


Bit of a long shot but try tweaking the baud rate in Carlos software.

Guessing you don't have any other devices on the rs485 connection. If you do you may also need to tweak the id of one of the devices to stop conflicts.


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duncangardiner avatar image duncangardiner commented ·

Hi @matt1309


I only have this one device on the rs485 USB connection. The Batteries I have use however are on the CebroGXs BMS-CAN which I understand is also a rs485 protocol, hence I wanted to move the ET122 ID away from 1, as this is an id my master battery's is set to. And now I have those communicating, so I would rather not mess with their Ids.


Further the Home Assistant Victron Yamal I grabbed from another HA user had the Energy Meter set with an ID of 30, so I thought I would assign that to mine as well. I figured if it worked for that guy, surely mine would work to.


Re the Buad rate? what do you recommend, just choosing a random number or is there a specific range of values Victron CebroGXs look for?


Kind regards


Duncan

0 Likes 0 ·
matt1309 avatar image matt1309 duncangardiner commented ·
Mines set to 9600, think that's the default though isn't it?



Do you get any lights flashing when connected to gx device like you see with Carlos software.



Also guessing firmwares are all up to date?

When you connect to Carlos software are you using the same adapter? If not I was going to say try swapping A and B wires around but if you're using same adapter to access Carlos software then that wouldn't explain it.

Then maybe this thread although I didn't have the issue mentioned here

0 Likes 0 ·
Show more comments
duncangardiner avatar image
duncangardiner answered ·

Hi @matt1309


Your a legend!


That post you sent me worked. Not all the SSH stuff at the top, but the last reply where radmin-1 uses the MProg SW Eprom tool. Apparently my issue is a preconfigured cable description, either the manufacture or Victron set, which is not aligned with the internal name of the USB converter I got sold. I just had to change the text in section "Product Description" from "USB-RS485-WE" to "FT232R USB UART" of the ET112's Eprom using the MProg SW by FTDI.

eprom-setting.jpg

Then of course I had to change the Baud rate back to 9600 and the Address ID back to 1 using the 'Carlo Gazzai' tool, and once I plugged the usb converter back into the CebroGX, all the lights started flashing and the Et112 popped up in my devices list as a grid meter!


What a faff. with out this forum. I'd be buggered, you guys and girls rock!


Take care Duncan


eprom-setting.jpg (251.4 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rgear13 avatar image rgear13 commented ·

Would you be so kind to tell me where I can get Mprog?


0 Likes 0 ·
rr-engineering avatar image rr-engineering rgear13 commented ·

This solution (changing product description string) worked for me too on a generic FTDI adaptor brought from ebay. I couldn't find mprog either but FT_prog from the FTDI utilities page did the job.


https://ftdichip.com/utilities/


1710242650771.png

1 Like 1 ·
1710242650771.png (161.3 KiB)
michelg avatar image
michelg answered ·

Hi Ducangardiner, have a look at my picture, almost same configuration and it works nicely. It seems the wires you are using are not the correct ones. By the way, take also a look at the path the cable is following, as I had some issues with parasites interfering with it...

https://community.victronenergy.com/questions/70286/energy-meter-et112-cerbo-gx.html

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duncangardiner avatar image duncangardiner commented ·
Hi @MichelG


I am using the same wires as in your photo Yellow, Orange and Black from the USB converter. I just lengthen that cable with a LAN cable which does not have the Yellow or Black coloured wires. So I use the Orange/White and Brown. Orange/white to the Yellow of the USB cable. Brown to the Black. This is as per the Victron how to wire an extension led to the ET112 usb cable.


As mentioned the ET112 and USB connector including the LAN cable extension, work fine when plugged directly into my laptop and I address the ET112 with either the manufactures software 'Carlo Gavazzi UCS Universal Configuration tool' and most recently a Eprom configuration tool 'MProg' by FTDI.

But the CebroGX. just does not want to see the ET112.

Its kicking my ass a bit.


0 Likes 0 ·
michelg avatar image michelg duncangardiner commented ·
Any chance to connect directly the USB wire to the ET112, without extending it ? If it works fine, this means the problem is related to interferences as I had at the beginning. Try to move the wire and find another path.
0 Likes 0 ·
fellside avatar image
fellside answered ·

You are plugged into one of the two lefthand usb ports? Righthand is power only.

Do you get flashing led's to show there is some communication going on?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duncangardiner avatar image duncangardiner commented ·
Hi @Fellside yes I am using the middle USB port of the Cebro GX. The use was not the cable. it turned out to be an EPROM setting in the Et122 itself. changing a Product description of a cable seemed to resolved the connection issues. See above.


Thanks for your input


Take Care Duncan

0 Likes 0 ·

Related Resources