question

duncangardiner avatar image
duncangardiner asked

RosenPV 200A 10kw Powerwall setup with Victron RS 450/100 charge controller

Hi I am new to everything Victron.

I have an eco system that consists of a MultiPlus II 48V 8000 inverter, a MPPT RS 450/100 Tr charge controller, and a CebroGX. I have 13 x 550w solar panels in 2 arrays (9 panels and 4 panels) one array per tracker channel on the RS 450/100. My Batteries (2 of) are RosenPV 48V 200A 10Kw Powerwall batteries.

I am working my way through the configuration and setup. The CebroGx was easy-ish although I had a terrible time getting it to connect to my home network (attaching a LAN cable crashes my router, and it took ages before it would connect to the wifi). Now its connected I can see the RS and Cebro.

The Rosen batteries did not come with any documentation that helps with setup. After a few emails to their sales team they had an engineer connect to my Laptop and via the Pylontech BS software and a USB adapter to an 232 port configure the batteries individually. They've set the CAN interface to PylonTech CAN rather than the available Victron CAN. And could not answer me when I asked about the Victron terminators (where on the Rosen batteries could I add the terminator (as there are multiple RS485 ports available but only one CAN port per battery).

Right now I can see power being generated by the solar panels and the current being pushed to the batteries. But I can not see state of charge and therefore do not know if the charge controller can either.

Further I can not find anywhere the Absorption Voltage, Charge Voltage, and float voltage settings the RS 450/100 is asking me to set in any documentation offered by RosenPV.

So I have used settings from what looks like a Rosen bench test that displays Factory Voltage, Voltage at end of discharge, and Charging Voltage.

I have asked RosenPV the question, but as yet no answer (they are 13 hours out of sync to me in Portugal).

So I was hoping someone on here as set up the RosenPV 48V 200amp Batteries before and can offer me some guidance as to the correct charge settings and CAN configuration.


All answers greatly appreciated


Duncan

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
matt1309 avatar image
matt1309 answered ·

Hi @Duncan.Gardiner

I'm not familiar with this brand but I had a quick search and found some manuals that might help:

Rosen-48V-200AH-LiFePo4-Battery-Powerwall.pdf (energyserv.ie)

photovoltaikforum.com/core/attachment/228535-rosen-48v-lifepo4-battery-powerwall-user-manual-006-compressed-1-pdf/

Assuming i've found the right battery manual, it looks like the batteries are 15 cells each (similar to pylontech). I personally set absorption to 3.45v per cell (3.45*15 = 51.75) and float at 3.375 (3.375*15 = 50.625).

However the spec sheet in first link has some less conservative specifications. (Note my settings are very conservative, a lot of folk will set 3.55 per cell for absorption)


In regards to your question on only one can port vs rs485 issue it looks like you daisy chains the batteries using RS485 and then to connect to inverter you use CAN. At least that's what's suggested on diagram using growatt inverter as an example. I'm not sure on victron compatibility but it is noted in the manual via CAN so assuming I've found the right manual it should work.


In regards to your router crashing when plugging in GX device via ethernet. It sounds to me like a DHCP issue, maybe where GX device is using an ip that is already in use or even on the wrong subnet. When you're connect to wifi you may want to try setting ethernet ip manually to an ip you know isn't taken on your network. You can do this in settings-> ethernet -> and change ip configuration to manual and enter the information yourself rather than relying on router DHCP server to assign the IP.

16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duncangardiner avatar image duncangardiner commented ·
@matt1309 thanks for this, your reply is very helpful. and Yes it looks like you found the correct manuals. Both seem to refer to the batteries I have, although the second may be older versions. As the case layout images are slightly different to what I have in real life.


I understand you maths. but I am still struggling to line up the voltage stats in the manuals to the settings I can apply in the Victron RS MMPT 450/100. The Manuals refer to Nominal Voltage, Charging Voltage, and End of Charge Voltage.

However a quick ChatGPT "please explain Absorption Voltage, Float Voltage and Equalization Voltage" got me back in the game.

Basically the theme is set these Victron settings all slightly higher than the batteries Nominal voltage. So between 52V and 54V in my case (as the Nominal Voltage is 48V). With Absorption being the middle ground, Float being the lowest and Equalization being the highest. So mine are going to 53V, 52V, 54V

Re the CAN. I am still not clear if I the RS485 Ports let me terminate the Victron CAN bus or not. I am going to adjust the Batteries CAN protocol to Victron and see if I get any state of charge data back to the MPPT controller. I have noted that the charge controller stopped charging the batteries so it may have had some indication that they reached max charge. but is just not displaying the results.

Re the Lan yes its weird. I do not think it was clashing I set the IP manually to an address I know was free. But whenever I plug the physical Lan cable into the Cebro, bad things happen at my router. So for now its wifi only.


Thanks again for the reply, I'll let you know how I get on.


Take Care


Duncan

0 Likes 0 ·
Show more comments
duncangardiner avatar image
duncangardiner answered ·

Ok here is a final note to describe what worked and how I got to the correct place. Also highlight what I got wrong.

Firstly its all up and running. I have the RosenPV batteries communicating between themselves. I have the RosenPV Batteries communicating to the VictronGX via the BMS-CAN port. I Have my RS MPPT 450/100 Tr Charge Controller communicating with two arrays of panels independently. The RS MPPT 450/100 Tr is communicating to the CebroGX via the VE_CAN port, and I have the Victron MultiPlus 48V8000 communicating to the CebroGX via the VE-BUS.

The easy bits:

As long as you build a solar array to the specifications of the Victron RS 450/100 TR Charge Controller (mine are an array of 9 550w panels at 41.96V(Max Power) and 13.11A(Max Power) and an array of 4 panels 550w at 41.9V and 13.11A). I plugged these two arrays into the RS MPPT 450/100 Tr via a DC disconnect break box and it just recognised everything and started using it.

The Victron MultiPlus 48V 8000 Inverter setup. Basically all I had to do was make sure the AC out port was not sending more than 50Amps, as houses here in Portugal have a main fuse of 40Amps for residential.

Connecting to the RS MPPT 450/100 Tr via Bluetooth. it just works and Victron connect makes the rest easy.

The CebroGX, set up and connecting to Victron VRM (once I had internet configured on the CebroGX.

The not so easy bits:

Getting my CebroGX to connect to the internet. My LAN connection still is not working. Whenever I plug in a LAN cable to this CebroGX, my router packs a massive sad and my internet for the entire house dies. On a plus note I learnt many interesting Lithuanian words to call Victron from my wife, while the internet was off. Once I got past my stupid Bluetooth mistake i did get the Wi-Fi connected, but it took several tries.

Where I went mostly wrong with my initial connection to the CebroGX was connecting my phone to Bluetooth to the CebroGX directly, before I had the Victron Connect app running. Dump mistake on my part. Android seems to grab the Bluetooth connection and will not let go, so and when Victron Connect tries to communicate with the device, it gets another phone is already connected error.


CABLES! I used the blue Victron cable to connect my Multiplus to the CebroGX on the VE-BUS which is correct. However I did not pay enough attention to the blue cable I used. It was a BMS-CAN cable type A so not configured for that purpose, BIG MISTAKE. Hence the CebroGX not being able to see the MultiPlus 48V8000 inverter when I powered it on. The MultiPlus 48V 8000 inverter communicates via a standard LAN CAT5e or CAT6 cable, once I figured out this error once you have the CebroGX running plugging in the MultiPlus via the VE-BUS immediately has it pop up in the CerbroGXs device list.


The RS MPPT 450/100 Tr Charge Controller, communicates on the VE-CAN port. the documentation states both ends of a VE-CAn needs to be terminated, this in my case turned out to be not true, with only the second port of the CebroGX needing the Victron Terminator. Plugging in a Standard LAN cable to both the CebroGX and the RS MPPT 450/100 Tr and terminating at the CebroGX end is enough to have thee two communicating correctly.


The RosenPV. Lets start with OMG their documentation and customer support is F^$%$ SH&^& !

The Powerwall 200A 10Kw batteries I have need the following.

  1. The internal configurations setting need to be changed. I was not able to do this alone. All you need to connect to the Batteries BMS is a converter cable they supplied and the Pylotech BMS software. However RosenPV have locked their BMS with a password.
  2. So I had to email them loads of times to get an engineer to come onto my laptop (yes I know very likely the Chinese gov has complete control of my laptop and bank account now). So he could unlock the BMS and change the Inverter protocol settings to:
    1. CAN Protocol to Victron_CAN
    2. RS485 Protocol to Pylon_485
  3. With the BMS setup. if you have two Batteries like I do, the DIM switches need to be set accordingly:
    1. Master Battery DIM to 1000
    2. First Slave Battery DIM to 0100
  4. Cables:
    1. I used a short Standard LAN patch cable it needs to go from Port 1 RS485 on the Master (leavening Port Zero empty, this tells the BMS its the Master Battery, something the bloody RosenPV guy did not even know!), to Port Zero of the RS485 on the first Slave Battery. If you had a third battery it would go from port 1 on the First Slave to port zero on the second slave and so on. Based on the Pylon Tech documentation I believe a chain of 14 batteries is the maximum
  5. From the CAN port on the Master RosenPV battery you plug in a Victron Type A cable. Polarity matters people read the cable. I got this soooo wrong so many times. The Victron end goes into the CebroGX via the BMS-CAN ports and the end marked Battery goes into the RosenPV master battery's CAN port.
  6. The Victron BMS-CAN port needs to be terminated. This also kicked my ass for a long time. I was under the miscomception that only the VE-CAN needed terminators. But NO, the BMS -CAN also uses one. I discovered this after watching avery helpful german guy on you tube tlak about PylonTech batteries and Victron CAN. Link here [Part 1] Connect Pylontech Battery to Victron Multiplus II . Ignore that fact he is using a MultiPlus the title he actually is using the CebroGX Can. In Part one he builds a Type B cable (I did that, it does not work with the RosenPV batteris). In part 2 he builds a TypeA, this works!. And then ofcourse I discovered I had a proper Victron Type A already just connected to my MultiPlus (IDIOT!).


Ok with everything cabled correctly. The CebroGX seeing all my Victron and RosenPV devices. It actually sees the RosenPV batteries as batteries called 'LEOCH' but at this stage I can see SOC the other Battery stats I need to move forward.


The Following photos should show what I have just described above.


20230811-145316.jpg


Ok from Left to Right:

  • The Victron Type A cable - the Victron end in the first BMS CAN Port, going to the CAN port of the ROSENPV Master Battery
  • A Victron Blue Terminator in the second BMS CAN port
  • A Victron Blue Terminator in the first VE Can Port
  • A Standard LAN CAT5e cable going to the VE CAN port of my RS MPPT 450/100
  • A Standard LAN cable in the first VE BUS port going to the VE Bus of the Victron MultiPlus 48V 8000 inverter.
  • A very empty LAN port Booooo Victron Booooo!











1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matt1309 avatar image matt1309 commented ·
Glad it's sorted. (Couldnt click on the youtube link but imagine most folk will guess it's Andy from Off grid garage based on your description)
0 Likes 0 ·
duncangardiner avatar image
duncangardiner answered ·

Some Additional Detail:


masterbattery.jpg


Here is a photo of my now Master Battery:

  • Note the Red Dim switches:
    • Switch 1 on first from the left up = 1
    • Switch 2 on second from the left down = 0
    • Switch 3 on second from the left down = 0
    • Switch 4 on second from the left down = 0
  • RS485 in CAN section - is empty
  • CAN Port has the other end of the Victron Type A cable (The Battery end as marked)
  • The 232 port this is where the converter cable the RosenPV engineer has you connect your laptop to when he makes changes to the BMS
  • The Left most RS485 port (Port Zero). On the Master battery it must be empty as per Helmut's description of PylonTech to Victron Can set up.
  • The Right most RS485 port (Port 1) has the short patch cable ( a Standard LAN cable just a short one) connected to port 0 of the Slave battery just above out of shot.

victron-remoteconsole-devicelist.jpg

The Money Shot!, all my device being seen by the CebroGX and communicating with each other.


victron-to-pylotech-cable-pin-out.jpg


A Type A cable PIN-OUT and yes you only need 3 wires from a 8 wire LAN cable to make this work. Its fiddly to make yourself but I did it and I am an Idiot so you can too. Or just use the Supplied one Victron gives you as I eventually did, after much swearing building my own first.


victron-vrm-devicelist.jpg


And just to prove Victron VRM sees things too.


victron-vrm-dashboard.jpg


Now I need a massive lay down, and possibly a big drink!