question

chrisriche avatar image
chrisriche asked

AC Input limit won’t go below 26.2A on a Cerbo GX

I have two Quattro 48/5000 running in parallel. For the AC Current Limit setting, editable on the Cerbo display, I can adjust it down but it just resets back to 26.2A when I press Accept.

Thoughts on what I’m doing wrong? Thanks!

MultiPlus Quattro Inverter Chargercerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
chrisriche avatar image
chrisriche answered ·

img-6225.jpegimg-6226.jpegHere are two photos of what I’m referring to.


img-6225.jpeg (3.5 MiB)
img-6226.jpeg (3.5 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisriche avatar image
chrisriche answered ·

Here’s a picture of the Quattro control panel. If i try setting it to 10a, for example, I get an error message.img-6255.png


img-6255.png (889.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image
seb71 answered ·

If Power Assist is enabled, there is a certain minimum value for AC input current limit, dependig on the inverter model. Probably that's the cause.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image
derrick thomas answered ·

Like seb71 said, the minimum input limit per inverter for your model is 13.4, you have 2 in parallel so it's doubled. (Yes I know the math doesn't add up exactly, it is an approximation.)