My BMS has two current sensors. One for charging currents and one for the loads. Is there any way to seperate the output from the charger from the input for the inverter of a Mulitplus 24/5000/120-100?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
My BMS has two current sensors. One for charging currents and one for the loads. Is there any way to seperate the output from the charger from the input for the inverter of a Mulitplus 24/5000/120-100?
The MultiPlus does not comprise of a separate charger and inverter. It comprises of a single converter which operates as a charger and then switches over to be an inverter depending on what role it needs to perform.
Therefore, as Kai said, it only has a single battery connection.
Thanks for the answers!
Hi Markus what sort of BMS is it.
if its a Smart123 then you can use just one sensor the load sensor and this will read by directional for you. the only down side is that the load and charge in and outs screen on the phone dont show any readings but the grand total in the middle works fine
Hi Paul, I'm using the ECS LiPro1-6 Active and the ECS Greenview (to get Modbus TCP). For this BMS I have to use two current sensors (HAL sensors) because they are not bidirectional. But it’s possible. The disadvantage is that I only get the difference of the currents and not their absolute values, and the need of more current sensors. But if there is no other way, I’m going to build it that way.