pfalzkind avatar image
pfalzkind asked
Multiplus II 48/3000/35-32: maximum AC input current refers to ?
When I look into the MPII datasheet, I see a "maximum AC input current" of 32 A. I wonder, if this value really refers only to AC-In ? Yes - it should be clear: AC input current should refer to AC-In. But I plan to connect a PV inverter (Fronius) to AC-Out1. So, looking from MPII point of view, AC current can come from AC-In and from AC-Out1.
Besides, also the 1:1 rule is a little bit difficult to obey in detail: Does 1:1 refer to the MPII "peak outpout power" (5500W) or the "continous output power @ nonlinear load" (3000 W) or the "continous output power" (2400 W) ?
I've choosen a Fronius 3.0-1 with 3000 W. Does it fit ?
Thank you
Pfalzkind
Multiplus-II
mvas avatar image
mvas answered ·
If there is 32 amps flowing into AC-IN, then explain how the Fronius will push any amps into the AC-OUT connection?
AC-IN really does means AC-IN. It could not be any clearer.
2. The Factor 1.0 Rule
The max PV power must be equal or less than the VA rating of the inverter/charger
If you read the entire "Factor 1.0 Rule" section, it is very clear.
It's the max current the MultiPlus can passthrough from AC IN to AC OUT. Theoretically also from OUT to IN but that would be more than the 1.0 rule.