MPPT 100V 50 amp 12/24-Volt Solar Charge Controller voltage jump TO 30V

I have a 100V 50-amp MPPT Solar Charge Controller intended for a 24V battery systems, along with a 1000W solar panel. When I turn the MPPT controller off (disconnect from the batter) and then on, it produces a 30V output, which causes the Battery Management System (BMS) to trip. I verified this behavior through testing then output on the MPPT. To resolve this issue, I found that turning off the power to the battery, then turning it back on, lets the BMS trip. Afterward, I can make any setting changes through the Victron app to fix it.

Is there a problem with the unit?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvas avatar image
mvas answered ·

Did you leave the PV connected and ON without a battery connected?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bore avatar image bore commented ·
Tried leaving it on and off still puts out 30v's
0 Likes 0 ·