tony-towers asked

3 phase different number of inverters per phase

Is it possible to have a three phase system with 4 x Quattro 48/5000/120 where 2 of them are in L1?

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Yes this is possible, but I don't know if it is also possible in a ESS system (I'll ask for you)

for more information:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

Update: it is indeed not supported for ESS systems.

2 |3000