Error2 BlueSolar

I'm running 6x Pylontech US5000 in parallel, linked via the CANbus to a CerboGX. Charging this I have 8 BlueSolar MPPT 150/35.


My MPPT are a mix of hardware rev2 and rev 3, rev 2 are running FW 1.61 and rev3 are running rev 1.59. Cerbo GX is F/W 2.91

The problem I have is that the FW1.61 MPPT units report battery overvoltage as soon as any charging starts - even if I replace the solar panels with a bench PSUand gradually increase the PV voltage. The only way to recover seems to be to disconnect VE.direct, PV and battery connections and restart it.


I can't seem to find a way to regress the F/W to 1.59, so I'm not sure what to check next Any ideas!


Thanks
Kevin

MPPT SmartSolar
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Are they all programmed the same?


Or have the blue solar just been programmed with the rotary switches?
0 Likes 0 ·
Show more comments
2 Answers
janlerouxrsa avatar image
janlerouxrsa answered ·

My MPPT 150/45 rev 3 firmware 1.61 is giving the same error.

https://community.victronenergy.com/questions/222867/blue-solar-mppt-15045-error-battery-high-voltage.html

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mrkev avatar image
mrkev answered ·

Ah interesting - I did suspect the F/W... the release note say the voltage detect algorithm changed!

In my case the MPPT is programmed to know it's got 48V batteries too.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.