CERBO GX, x3 RS 450/100 and the Inverters x2 all on CAN. 48v 1800ah Battery bank on busbar.
Hi i have two inverters in parallel and they are working fine but i have a question to the load they share...
This might be normal but i would like to know for sure, i have an 80w load difference between the two (the new Inverter always has the higher load compared to the older one, purchased about eight months apart), it does not matter if the load is low (100 to 200w each) or high (2000 to 3000w + each).
The wiring is exactly the same from the DC BUS (busbar) to the Inverters and on the AC side (10mm2 "@1m soft multi-core copper/silicone wire) going from the Inverters to the main AC Distibution point. The DC ripple never goes above 0.05v. All bolts are torqued to the correct torque setting and checked.
I guess it's either the difference between the two inverters or the way it meant to be. Anyone with any ideas/experience or comments please. (PS - i don't like guessing!)