I have the strangest issue;
In The Netherlands we have a "smart meter" and in my case I even have 3 individual 25A main breakers, one for each fase, that I can turn off. If I do that, the smart meter indicates which fase number is failing.
Other than that I have the basic setup for HomeAssistant for the smart meter so I can read and store every detail about the individual phases.
Still, with all these certainties, the multi's throw a phase rotation error when I start the system. If I swap phase 2 and 3 the ESS boots and all is working normally. However, if I change the config from sum of all phases to individual phase, the ESS obviously goes horrible wrong as it's feeding to grid on phase 2 to reach a set point measured on phase 3.
Basically, all phase related information from HomeAssistant and the Victron cloud is correct. All readings add up and work fine. Except for that fact that multis 2 and 3 feed from/to the wrong phase.
Someone please point me in the right direction here :-) I have ordered a phase sequence meter to re-confirm but all readings and tests and wiring add up AND I have various 3 fase appliances like 2 car chargers and a heat pump that work fine
The multis are configured for ESS only. Nothing connected or configured on the outputs. Solar is grid parallel (Enphase). The 3 multis share 0, each have their phase and ground is only connected to ac-in and chassis.
Thanks