MPPT 100/50 Low Output

I have a Victron MPPT 100/50 charge controller (firmware v1.61) charging a 1180ah 12v LiFePo4 battery bank. I have two 370w panels, flat mounted, on the roof, wired in parallel. When both panels are connected at high noon, sunny skies, I get about 315w to the battery. Each panel is showing about 35v and ~4.5amps, with the charger outputting ~13.5v @ ~23a. Seemed a bit low.

Note that my battery system is currently at only 30% SOC since I've had the solar disconnected for a couple weeks. So there's plenty of room left to accept amps. When I hook to shore power, I have no problem feeding in 100a to these batteries.

To test, I decided to isolate each individual panel. I hooked panel one up directly to the charge controller and saw the same output voltage from the charger. 315w. Obviously the amperage from the panel was greater, at 9a.

Second panel had the same when hooked up to the charge controller by itself. 315w max output at the batteries.

To further test, I tried wiring the two panels in series to the 100/50 MPPT. Voltages doubled, amperage halved, still 315w output with the two panels.

Something is limiting the charge current, and I do not understand what it is. I would expect to be getting 630w to the batteries from this setup given that each panel individually is charging at 315w.

I am not running DVCC on the system. The charge limit on the MPPT controller is set to maximum 50a, but I'm not able to get anywhere close to that. Absorption voltage is 14.2v, float is 13.6v.

As an aside, but potentially related, I noticed that the MPPT really wanted to go to float early. I have no idea why the MPPT controller would even leave bulk at such a low SOC, much less go to float. Also, my float voltage is 13.6 in the MPPT settings, and while in float, the battery voltage was only 13.35. Re-bulk voltage offset is .1v, so I would've expected the controller to go back to bulk with the voltage down at 13.35

Any ideas would be much appreciated.


Thanks,
Sam

MPPT SmartSolar
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvas avatar image mvas commented ·

Is your Solar Charger Controller communicating with any other device? What is the output voltage of the Solar Charger at the MPPT terminals? Same as the battery terminals? Post images of your PV Panel, Battery & Charger configuration, while charging. Have you performed a power-down reset of the SCC?

1 Like 1 ·
samelmore avatar image samelmore mvas commented ·
The MPPT SCC is in a VEDirect network attached to the Cerbo. It's shown as Standalone for network status on the Cerbo. Output voltage at the MPPT is around 13.6v when it's charging, battery voltage at the BMV is showing 13.35v.

I disabled and re-enabled the SCC as part of my testing. I have not completely cut power.

0 Likes 0 ·
mvas avatar image mvas samelmore commented ·

Bluetooth to the MPPT parameters?

0 Likes 0 ·
samelmore avatar image samelmore mvas commented ·
Thanks for taking the time, @mvas to read and respond, looks like a reboot did the trick.
0 Likes 0 ·
1 Answer
samelmore avatar image
samelmore answered ·

I guess the answer is rebooting. Or, in my case, just switching the controller from user defined to preset and then back to user-defined on the battery settings. User defined settings were put back to the exact same ones as before, but now suddenly I'm getting 370w at 9:30am, which seems correct (yesterday I was only getting about 150w at that time)

When in doubt, reboot. Just like Windows 3.1.