Got a Quattro 12/5000/220-2x100 120V running firmware 2733430. (Same system as in this old post.) Since then, I've beefed up the shoreline to a true 20A circuit, and adjusted the input limit to 20A accordingly.
Sometimes the system will happily draw 19.8A from the shore, and sometimes it'll limit itself at 11.6A and go into PowerAssist for my roughly-2kW load.
Here's the weird thing: If I increment the input current limit just a little, the actual power drawn from the shore increases dramatically. Here's my observational data:
Current limit set in VEConfigure | Actual current drawn | Load and status |
20A | 11.6A | 2kw, PowerAssist assisting |
21A | 12.6A | 2kw, PowerAssist assisting |
21.5A | 20.2A | 2kw, battery charging |
22A | 20.7A | 2kw, battery charging |
30A | 27A | 2kw, battery charging |
AC input voltage is roughly 108-112V in all cases.
So why the huge jump in actual current, for a tiny bump in the set limit? It's not correlated with input voltage, and I can't identify anything this behavior is correlated with. I've tried setting WeakAC and it had no effect on the behavior either way. Shore power is 60Hz grid AC, so it's not like a generator is lagging its frequency or anything. What else should I be checking?
For the moment, I'm leaving it at 21.5A to keep the battery from draining while on shore power, even though it slightly overdraws the circuit's nominal rating, the breaker doesn't actually trip until a bit higher than that. ;)