SmartSolar: please help me to decide

Given a Victron SmartSolar MPPT 250/70-Tr VE.Can and I have 6 pieces of 460Watt el cheapo Chinese PV panel. The max Voc on paper 41V but I measure only 38-39V in mid summer as max. So the 250V MPPT could deal with them in series too. Question: Should I wire the 6 panels in series or 2 x 3 for this type of MPPT?

MPPT SmartSolar
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Type in the full specs into the MPPT sizing calc.

You have to allow for cooler weather when Voltage increases and would then overload the MPPT.

246V is too close to the limit, rather split into into 2 x 3, or get an RS450, but that is more expensive and overkill, unless you are planning on upgrading in the future.

2 Likes 2 ·
Show more comments
2 Answers
mvas avatar image
mvas answered ·

2 x 3 in series! Do not even think about 6 in series.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

belmont avatar image
belmont answered ·

thanks for all, clear, i will do 2x3 then