I'm having a bit of an issue so I'm looking for a little clarification on what is supposed to happen when running a backup generator on an ESS system. I have parallel mp2 24/3000 2x120. I understand that ESS uses frequency shifting to control feed in and so on and so forth. When running a little Honda 2k inverter generator for backup everything works as expected, stable voltage and frequency, batteries charging. When running my 7.5k Kubota the frequency constantly moves up and down between about 56 and 65 which causes the generator output to fluctuate, voltage is not steady (bounces between about 110 and 135) and causes the DC output (inverter charger output) to fluctuate up and down about 50 amps or so. I have grid code set to "other" with lom disabled. (Yes I have anti islanding protection) Weak ac input is not selected. when I disable ESS and run the 7.5k Genny it is absolutely stable voltage and frequency all the way up to full rated output so I don't believe it's a problem with the generator, but maybe just an issue with the way ESS works with this particular generator. When running a backup generator "generator" is selected as the input source.

I'm assuming that there is no way to temporarily disable ESS while running a generator, other than removing the assistant?

Is this expected behavior? Meaning... wouldn't it be desirable to disable ESS while a generator is running anyway? Or at least disable frequency shifting while running so the multi only synchronizes to the incoming ac rather than trying to push/pull the frequency back to the generator?

I'm still learning so go easy on me. I'm a pretty quick study though.

ESSGenerator
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@derrick thomas

You generator does not have a stable way of regulating itself. Which will be the main issue.

When working with generators the impedence is different to that of the grid. So does behave differently. You have LOM disabled that disabled the push back to 'grid'.

Try enabling the weak AC, but also lower your input current limit.

The other way is to increase grid set point a bit as well. But do one at a time to see which one works to help your generator stabilise.

0 Likes 0 ·
Show more comments
1 Answer
multiplusinus avatar image
multiplusinus answered ·

ESS "tugs" at the grid by varying the frequency up and down. It does this varying the frequency slightly, which could explain what you are seeing. And the reason that ESS does this is to try to figure out if the connection is really the grid, in which case the shift wouldn't result in any input changes, or some other source like a generator.