Multiplus BoostFactor

Hello Victron Team,

Can you explain me what exactly is the "BoostFactor"?
Thank you

Kind regards
Pablo

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi Botnic, please use the help function in VEConfigure. Its the go to place for all these kind of questions.



boostfactor.png (337.2 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lucasnowak avatar image lucasnowak commented ·

Hi, so a quick case study question.

We have a system with Quattro 8k/230V with input current limit set on 60A and Power Assist Boost ratio is set to 2.0.

How let's assume we have an abrupt load request - Quattro assumes 2.0*60A current (according to the manual). And at that moment what does it exactly do?

1. Would it prepare those 120A from the batteries? If such, does it ease the input for a few cycles and inverts power from the battery?

2. Would it keep 60A from the input and add 60A from the batteries?


The below chart shows currents active and reactive and THD (sorry for LQ graph, hope it's readable) on the input of Quattro (actually output from grid inverter). It looks like when power assist kicks in, it eases the input for a "second", adds power from DC and brings input current to a previous state.

It's worth mentioning it's not happening always, but at times, which is strange.

0 Likes 0 ·
Martin Měkota avatar image Martin Měkota commented ·

Hi, I have some questions extra. The help in VE Configure dosen´t seem to be very clear for me.

When Multi switches to sassist mode, will the inverter provide always current = AC IN current limit * boost factor ?

Than, this provided current is still the same and Multi will drive AC IN current according to the need? Or the current provided by inverter wil be regulated after some time according to need to keep AC IN current on maximal limit?

If AC IN current limit * boost factor is higher than a maximal power of inverter, than Multi trimms maximal provided power or it falls to allarm and mistake?

I can use assistant "input current limit control" to drive AC IN limit by AUX. Than Multi counts the assist current from AC IN limit set on a "General" card of a VE Config, or from limit driven by AUX?

Thank you for your reply.

Martin

0 Likes 0 ·
Martin Měkota avatar image Martin Měkota Martin Měkota commented ·

After some tests I´m able to reply myself. I did not measured exactly, only watched what Multi is doing...

When Multi switches to sassist mode, will the inverter provide always current = AC IN current limit * boost factor ?

Yes, but often it is not possible, so it just gives maximal possible current.

Than, this provided current is still the same and Multi will drive AC IN current according to the need?

No.

Or the current provided by inverter wil be regulated after some time according to need to keep AC IN current on maximal limit?

Yes, after cca 0,5s inverter regulates it´s power to normal power assist function.

If AC IN current limit * boost factor is higher than a maximal power of inverter, than Multi trimms maximal provided power or it falls to allarm and mistake?

I still don´t know, but moment using boost factor is so short, so i thing inverter never falls to mistake. If needed power is too big, it probably falls to mistake later anyway...

I can use assistant "input current limit control" to drive AC IN limit by AUX. Than Multi counts the assist current from AC IN limit set on a "General" card of a VE Config, or from limit driven by AUX?

From currently set limit - given by assistant at this case.

Thank you for your reply.

Oh, that´s a pleasure!

Martin

0 Likes 0 ·
wkirby avatar image
wkirby answered ·

I think this is related to your other question.
However, it is normally recommended to be at 2.0. It is the peak power that the inverter will provide when shore current is no enough.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nightcrawler avatar image nightcrawler commented ·

So, for normal operation, it is recommended to be set to 2.0. Does this mean that if my AC current limit is set to 9 amps that it would provide up to 18 amps?

Also, What scenarios could arise where this value would be better set to another value either higher or lower?

0 Likes 0 ·
markus avatar image markus ♦♦ nightcrawler commented ·

see below. This has nothing to do with continuous output power. This setting only helps the inverter setting its voltage/power when Power Assist kicks in. It is regulated ms after anyway.

0 Likes 0 ·
nightcrawler avatar image nightcrawler markus ♦♦ commented ·

Thanks! I've never quite understood what that setting was there for until now.

0 Likes 0 ·
markus avatar image markus ♦♦ nightcrawler commented ·

welcome :o)

0 Likes 0 ·
botnic avatar image botnic commented ·

No. Not directly connected to the other question. It is recomended to set the Boostfactor to 1.2 by the FischerPanda manual.

0 Likes 0 ·
markus avatar image
markus answered ·

Boost Power Ratio to be expected, if the inverter has to assist. WKirby was faster. :o)

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markus avatar image markus ♦♦ commented ·

If you set this factor too high, you will have Overvoltage Peaks, when Power Assist kicks in.

If you set this factor too low, Power Assist might not work properly.

0 Likes 0 ·