Oh Hello guys
when I synchronise my battery manually , I get 100%. After that, the condition only reduces.
Does anyone have an idea which value I have set incorrectly?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Oh Hello guys
when I synchronise my battery manually , I get 100%. After that, the condition only reduces.
Does anyone have an idea which value I have set incorrectly?
You have likely incorrectly wired the system.
The ONLY thing that should be connected to the (-) side of your battery is the shunt. EVERYTHING else must be on the other side of the shunt:
Since you only see SoC decreasing, I suspect you have connected your charger either directly to the battery or to the battery side of the shunt.
Thank you!
Then I misunderstood the manual. The minus from the MppT controller must also be connected to the shunt and not to the battery , correct?
Sketched where the MPPT wires should go:
If you have a battery protect in the power circuit for the inverter, this is not permitted.
Thanks for the clarification. You speak in the plural. But you certainly mean only the negative connecter from the MPPT comes to the shunt, right?
Yes, it's an inverter. I still have to save some money for one from Victron. Is it not allowed to take power directly from the BP? So I still need a distribution bar? Then is misunderstood the manual.
Correct. (-) only. I got confused by the use of black for all cables.
Battery protect:
Diagram shows it for "DC Loads":
An inverter is not a DC load. It is a device that powers AC loads.
Manual: