why does solar not fully supply load and draw 50% from battery?

Victron 100/70, 1000W renology panels, 3000W AIMS inverter, 620 Ah lithium batteries on truck camper. When battery full (or nearly full) and in float mode and AC is on, the 55 amps needed to run AC is not provided by solar - instead its about a 50% battery/ 50% solar split. I want to run AC on solar during daytime and conserve battery for nightime use.

solar
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jacobjned avatar image jacobjned commented ·

A quick one, kindly confirm, that you mean Victron MPPT 150/70? Can you please share a screenshot of the settings you have used.
If I work on, 55A x 12V = 660W, does your MPPT via the VictronConnect app show that '300Wish' as PV generation?

0 Likes 0 ·
Show more comments
kevgermany avatar image kevgermany ♦♦ commented ·
Once the MPPT goes into float, it will stay there until battery voltage drops. With lithium, this can take a while due to the flat discharge curve.

There's a rebulk offset setting in the MPPT. Battery voltage needs to drop below float by this amount before the MPPT comes out of float. Try reducing this. You may need to tweak it a few times. You may wish to increase float voltage as well, but stay within battery maker's recommendation