I would like some input on the following design, just to make sure I understood everything correctly.
BYD Battery-Box Premium LVS 24.0
Adhering to the minimum battery size: 1,5kWp AC-tied PV Power = 4,8 kWh battery
So, 24 kWh/4,8kWh = 5
So, max installed PV AC is 5*1,5kWp = 7500 Wp max
Fronius Primo 8.2-1
max 8200W, which is smaller than 7500 Wp solar installed, so I will not use the Fronius to its full capacity.
Victron Quattro 48/15000/200-100/100
Following the 1.0 rule (max PV Power (min of installed solar or installed grid-tie inverter) =< VA rating of inverter/charger.)
So, 7500 Wp installed AC tied solar =< 15000VA. So, this is ok as well.
Luxor ECO LINE P72/330W
7500 Wp/330 Wp = 22,7 => 22 panels connected to the Fronius.
Is this correct or am I missing something?
Thanks,
Stijn