Negative feed showing to static genset

VRM is showing between 250-500w feeding into static generator? Just had some heavy storms, could this be causing some leakage via the generator?img-1273.png

VRM
img-1273.png (211.3 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Nigel

Slightly concerning as the input relays should be open if there is no AC present at the input.

You would need to check if they are open or not.

What is the LOM set to?

0 Likes 0 ·
Paul B avatar image Paul B commented ·
please measure the voltage at ac1 in with the generator stopped. the voltage should be zero. if its not diagnose why
0 Likes 0 ·