question

hindssight avatar image
hindssight asked

Not seeing Pylontech US2000B (Battery Monitor) in device list

Hello,


I have the following equipment installed:

1 x Quattro 48/8000 230V

2 x MPPT Smart Charge Controllers 250/100 MC4

8 x Pylontech US2000B Batteries

1 x Venus GX


The batteries are connected to the Venus through one Can port using the VE Can Cable Type B and the dummy plug is inserted in the other port. However, the Venus isn't recognising the Pylontech, it isn't shown in either the device list for the installation (usually shown under battery monitor) or in the device list section of the remote console.

Can-bus profile is set to Can-Bus BMS (500 kbit/s) and DVCC is enabled. Venus is on firmware 2.31 and Quattro is on 459.

Battery monitor under System Setup is set to Automatic but it appears to have auto selected the Quattro on VE Bus and the BMS is set as Off and doesn't give me the option to change it.


Please help me to enable the Pylontech BMS to act as the battery monitor.


Thanks


Pylontechinstallation
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Are you sure the battery is switched on?

Can you post some pictures of the installation, showing all the connections?

0 Likes 0 ·
hindssight avatar image hindssight Guy Stewart (Victron Community Manager) ♦♦ commented ·

Thanks, i'll take some photos of the installation and the connections when I go back out there on Sunday, but this installation has been set up identical to two others with Pylontech batteries and in those the batteries are visible.


Should I attempt to reset the Quattro and Venus and reconfigure again to see if it takes?

0 Likes 0 ·
Show more comments
3 Answers
Murray van Graan avatar image
Murray van Graan answered ·

Have you tried swopping the Can cable around and see if that has an effect? The cable has a battery end and a Venus device end as far as I know

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hindssight avatar image hindssight commented ·

Thanks, I have tried this as well, to no avail.

0 Likes 0 ·
jhass1 avatar image
jhass1 answered ·

I have the same problem. Did you get it resolved?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Do you use the "VE.Can to battery Can type B" cable in the right direction?

The VE.Can side at CCGX/Venus and battery Can side at the battery?!

0 Likes 0 ·
gary-c avatar image
gary-c answered ·

Hi I have the same issue with a multiplus 2. Ccgx and US3000 pylontech batteries. I rebooted the ccgx but not the inverter. Is that a requirement to detect the batteries on the ccgx. I have the correct cable and it's connected the correct way around. Any other suggestions. I will need to go back to site

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @gary c It should not be necessary to restart the multi.

There are many steps, such as setting the VE.Can port to 500kbps.

They are all listed here :

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

0 Likes 0 ·
nemo5 avatar image nemo5 Guy Stewart (Victron Community Manager) ♦♦ commented ·

Did you already solve your issue? As I have the same problem with same setup I wanted to know the solution.

0 Likes 0 ·

Related Resources

Victron Pylontech battery compatibility guide

Additional resources still need to be added for this topic