desert-rat asked

Load Current

I have two Vectron MPPT 100-50 controllers connected to 1000 watts of solar and then to four 12 volt 170 ah lithium batteries.

When the controller goes into float mode it does not seem to be able to supply the existing load current. I still have plenty of solar power, but the batteries start to discharge for some reason. After an hour or two they are down to around 98%.

Thanks


float
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@Desert Rat

Check your rebulk offset on the mppts.

Have you edited a Lithium profile preset when programmed for your batteries?

1 Like 1 ·
Show more comments
snoobler avatar image snoobler commented ·
You say you have two Victron 100/50 connected to 1000W of solar. Please confirm that these controllers are connected to two separate arrays totalling 1000W and not connected to the same 1000W array.


Each MPPT must have its own array.

0 Likes 0 ·