Multipluss II limited grid feed instable

I have my Multiplus II 48/3000 configured the Cerbo-S GX (FW 2.88) to feed PV excess to the grid, but with a limit of 600W. However, the feed in is not stable. It goes to -600W feed in, and then reduces roughly back to the grid setpoint, then it goes up again to -600W, and back down, and it keeps looping like that. If I set it to unlimited feed in it works with a constant feed in of -2300W and no drops whatsoever.


On the DC side there are several Victron MPPTs all controlled externally by the GX and a 15kWh Battery, so there is enough DC Power available for a stable feed. What did I do wrong?

bild-2023-06-13-123128983.pngbild-2023-06-13-123428153.png

Multiplus-IIfeed-in limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
matt1309 avatar image
matt1309 answered ·

Hi @Polly Nowak


Try enabling shared voltage sense in DVCC on cerbo gx?


I had similar issues where MPPT would turn on and off repeatedly when reaching the Maximum feed-in limit. Which for me just resulted in small peaks in battery voltage but maybe in your setup/with more MPPT's that's overflowing to AC side? Long shot but maybe the cause.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

polly-nowak avatar image
polly-nowak answered ·

Thank you for the reply. I tried it, but unfortunately, it did not solve the problem.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matt1309 avatar image matt1309 commented ·

Guessing you've tried this but checking connections on MPPT to cerbo, and maybe just giving everything a reboot. SVS was what sorted it for me.


Can you see anything unusual happening on the DC side. Do the spikes correspond with MPPTs turning on and off?

0 Likes 0 ·
polly-nowak avatar image polly-nowak matt1309 commented ·

The problem isn't that new, so I tried a few hardware things. The issue remains eventho I replaced MPPTs, rewired them. I rearranged the strings. And it isn't that the MPPTs turn themselves off. They just all go down to a few watts to meet the requirements of the AC Home Load. The Zero Feed in works absolutely flawless. The MPPTs work at high, and mostly stable power as well, since we have cloudless sunshine since more or less a few weeks. Until the Battery is charged at least. Then everything cuts back. If I turn on a high load like an oven or similar Loads, the Multiplus II delivers constant power to keep the AC Meter near zero and the MPPTs all fire up to prevent Battery discharge. But as great as all of that works, the limited excess feed in remains unstable. Unfortunately the Datalogging of VRM is to slow to tell whether the Multiplus is following the MPPTs or the other way around. Maybe I should invest in a PDA.

0 Likes 0 ·
szdan avatar image
szdan answered ·

Did you ever find a solution to this?