Disabling pass through on Multiplus ii

I have a European 220V 50hz boat and do not want a Multiplus II to pass through 60hz when I am at marinas where the available 220V is 60hz. This can cause malfunction of my microwave and clothes washer and is not optimal for my AC. However, I do like that the Multiplus II can provide both battery charging and function as an inverter. I have been told that you can use MK3-USB to configure the Multiplus II to disable the pass through, but I cannot find this described in the Victron manuals. Can anyone tell me where this configuration is described?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

If you look at the schematic in the manual you see that the AC OUT 1 is directly wired to the AC IN. AC OUT 1 can't be switched.

You can configure AC OUT 2 but I'm not sure if you can use the frequency for that.

I guess you need to use a separate charger for 60Hz shore power.