Venus upgrade

Bonjour,

Y a t-il une coupure de la sortie AC sur l'onduleur lorsqu'on fait un upgrade du firmware Venus ?

En bref, peut-on mettre à jour le Cerbo sans géner les utilisateurs connectés a la sortie AC ?


cerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
derrick thomas avatar image
derrick thomas answered ·

Depending on how it is configured, if there is ESS it may switch to "passthru" when communication is lost between the cerbo and the inverter. Otherwise, no.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lalluyn avatar image
lalluyn answered ·

Donc pas de coupure coté sortie AC si ESS installé et configuré ?


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image derrick thomas commented ·
There should be no cut in power as long as grid power is available at the time of upgrade.