question

lazza avatar image
lazza asked

What happens in ESS mode when grid voltage drops?

HI

A quick question on ESS fuctionality.

I understand that in case of grid-failure an ESS system will automatically switch to inverter + battery mode.

However, what happens if the voltage of the grid simply drops to 150V for say 30 seconds, for example?? ... and then returns

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

Hi Lazza, the default or set Grid settings in the inverter would apply

the default disconect settings are 180v so if you dropped to 150 the inverter would disconect and then reconect when the volatge increased to 187

the Low discount and the reconect voltages can be adjusted using VE Config.


the same happens on a high voltage as well


This is described in the Grid Section of the VEConfigure manual.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lazza avatar image lazza commented ·

Thanks for the reply... I thought that might be the case, but wanted to make sure

0 Likes 0 ·