question

tjorven avatar image
tjorven asked

I can't get my mppt to load

I can't get the Mppt solar to charge only float when I set it to the Cerbo. I get only float.

How can I fix it?I can't get any A from it.

Stefan

img-1650.png img-1651.png img-1647.jpeg

MPPT SmartSolar
img-1650.png (237.1 KiB)
img-1647.jpeg (5.4 MiB)
img-1651.png (407.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

What MPPT do you have?

Check all connections and fuses between the MPPT and the battery.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tjorven avatar image
tjorven answered ·

Hi i have checked the wiring and fuse, and they are correct. This morning i took away the solar connection to let the Mppt to take the battery voltage like a new installation. But now it says Absorbation but no amps. 21,86v 0,00A 0W.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

giampaolo avatar image
giampaolo answered ·

Have you checked if charging is allowed in the BMS settings. I would also check the PV voltage with a multimeter.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tjorven avatar image
tjorven answered ·

No, but the only changes are that i got the connection to the Cerbo. That’s the only changes since last year. The last picture is today in absorbation but still no Amps. .e5f20594-6595-4342-8827-d64f0498118b.pngff3c9a2e-b84a-4806-a41a-ac1cd66c252b.pngImage Caption


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
@Tjorven Have you checked the fuse between the mppt and battery??
0 Likes 0 ·
tjorven avatar image
tjorven answered ·

Hi i checked this. The only changes are that i have an Cerbo that’s connected to the mppt. Still different picture 1 yesterday pic2 today but no amps.b3add502-21ea-4ebb-8488-c4d90a2aa891.png986b7145-0b26-416a-9c0b-697b33ca43fc.pngImage Caption


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
@Tjorven Measure the voltage with a multimeter at the battery, and the battery terminals of the mppt.

Report back with voltages.

0 Likes 0 ·
giampaolo avatar image
giampaolo answered ·

Give also a look at Settings -- > Battery

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.