What is the minimum input current limit for Quattro?

Setting it on VEconfigure allows me to set it as low as I want. However, the input current limit won't go below 10.5 on the Colour Control.

It needs to be set lower as the customer only has a small generator. How do I do this?

CCGX Color ControlGeneratorVEConfigure 3input current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi Mick,

The minimum AC input current limits vary depending on the device, they are described in this article:

https://www.victronenergy.com/blog/2018/04/20/multiplus-quattro-inverter-chargers-improved-current-limits/

The definitive source for these AC input Power assist minimum current limits is here, you will need a Victron Professional account to access them.


If you wish to go lower than that, you must disable the PowerAssist feature.

It would also be a good idea for you to check out this MultiPlus Generator FAQ, if you haven't already.

https://www.victronenergy.com/live/multiplus_faq


8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pganguet avatar image pganguet commented ·

Guy, Can Victron update the minimum current limits spreadsheet to include the multiplus 2 data? Is it the same as the original multiplus?

0 Likes 0 ·
Show more comments
malcolmdmoore avatar image malcolmdmoore commented ·

Hi,

this doesn’t explain why CCGX only lets you set a limit below a certain number (15.5 in my case) when inverting.

0 Likes 0 ·
Show more comments
jbakuwel avatar image jbakuwel commented ·

Hi Guy,

I have a use case to dynamically limit the input current of a MultiPlus-II. Are there any concerns frequently updating this input limit current or can I update that limit to my hearts content?

Or to rephrase the question: am I wearing out internal (flash) memory in the Multi by repeatedly updating the input current limit?

My use case is an installation with two independent power systems (off grid) where the second system can assist the first system depending on the SOC of it's battery and the excess solar energy available there.

cheers,
Jan

0 Likes 0 ·