We have just installed 12 x pylontech US3000 with a hub for 2 racks of 6. The BMS is correctly communicating the DCL, but not the CCL. The CCL and DCL should be equal and the CCL is exactly half that of the DCL, which makes me believe that the BMS is only communication the CCL of one rack, not both. (cant be temperature issue as we are at 30ºC here)
This poses quite a problem. I have already noted that, although the Pylontech website and suppliers say that the US3000 can go up to 12 batteries without a hub, this isnt the case. If you do this, only 8 will be recognised by the Master (exactly the same as the other models). Therefore a hub is required.
I hope this CCL issue isnt another error!! Has anyone else heard of this issue? Is there a work-around?
Thanks