Easy Solar 5000 not responding to AC input

Hi, my Easysolar 5000/48 has been shurt down for a 6 month period, and batteries are flat (23v). When i connect to mains there is no responce from the multiplus. no responce by the color controller either.

i have checked the connection to the Input breaker, that is fine.

Batteries and solar are isolated.

what have i missed?

smart solar set-up help
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
andreas-siebenmorgen avatar image
andreas-siebenmorgen answered ·

Did you turn on the Power switch on the device?

Did you precharge the battery to its system voltage? The starting voltage of the EasySolar is at about 38 volts!

What kind of Battery are you using?

If you drained lead acid from 48V to 23V they will be dead.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Don’t start a multi without batteries. Besides being unsupported it is a good way to damage input relays.