I have Quattro 48/10000, it has the grid on AC in 1, and everything else on AC Out 1. So I have my incoming grid connection which goes through my smart meter then connects to AC in 1. All consumed energy is on AC out 1.
This means the Quattro is measuring power going to and from the grind, but the energy imported and exported as shown in the VRM does not match my smart meter data, I've only noticed this as I've added another battery and therefore import/export more each day.
VRM from grid | Smart Meter Import | Difference | VRM to grid | Smart meter export | Difference | |
Thursday | 15 | 14.21 | 0.79 | 50 | 47.89 | 2.11 |
Friday | 14.75 | 13.89 | 0.86 | 45 | 42.59 | 2.41 |
Saturday | 14.96 | 14.27 | 0.69 | 48 | 46.16 | 1.84 |
Sunday | 14.47 | 13.94 | 0.53 | 43 | 41.36 | 1.64 |
Monday | 21.81 | 20.91 | 0.9 | 26 | 24.74 | 1.26 |
Tuesday | 21.85 | 20.84 | 1.01 | 49 | 47.25 | 1.75 |
Wednesday | 21.79 | 20.66 | 1.13 | 51 | 48.85 | 2.15 |
I can't find a way to get the exact VRM to grid value, so these are the rounded values that the VRM shows daily, but it still illustrates the point that the values are off.
Any idea what's causing this, surely the energy meter in the Quattro is not that inaccurate?
I am of course assuming my Smart meter is accurate - this was new a couple of months ago.