How does a 3 Phase quattro deal with a lost supply phase?

Hi . What happens if the mains supply to a 3 phase ( 3 x 5 KW) quattro loses a phase?

Does the whole system change onto battery, or will it continue charging off 2 phases and give a normal 3 phase output?

3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The whole system will switch to inverter mode.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ralpht avatar image
ralpht answered ·

Thanks Matthias. So in Inverter mode, will the 2 quattros that still have mains supply keep topping up the battery?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image sharpener commented ·

If all three are in inverter mode the quattros will be disconnected from the grid as described in this thread.