question

marekp avatar image
marekp asked

ESS manual - DC-coupled PV - feed in excess - incorrect information?

I found this statement in the ESS Manual.

https://www.victronenergy.com.au/media/pg/Energy_Storage_System/en/configuration.html

4.3.4. Feed-in excess solar charger power
Set to 'On' to make the solar charger always operate at its maximum power point. The first priority is powering the loads, and the second priority is to charge the battery. If more power is available when those two priorities are met, then that power will be fed to the utility grid.
Please note that when enabling this option, the DVCC charge current limit configured under Settings → Limit charge current won't be active. The solar charger will operate at full power for maximum feed-in into the grid. It's advisable to configure a safe limit on the solar chargers when used with a small battery bank.

In my system when, in ESS, I turn "DC-coupled PV - feed in excess" ON, I still have the DVCC option "Limit charge current" active.

Is ESS manual in error?

cclecc
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
nickdb avatar image
nickdb answered ·

The option and setting remains, it will just be ignored.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@nickdb

The information in ESS manual suggests that CCL option is not active at all.

In reality it is active but only for inverter/charger.

When you have DC excess feeding "ON" and you set the CCL to ZERO, the inverter/charger will not charge the battery, but MPPT will.

1 Like 1 ·
nickdb avatar image nickdb ♦♦ marekp commented ·
Most ESS systems rely on solar to charge, so the docs are quite accurate in that respect and since the setting is intended to be global (since DVCC coordinates charging across all devices), saying it isn't active seems like a reasonable statement to make.
0 Likes 0 ·
Show more comments
pedaaa avatar image
pedaaa answered ·

you cannot remove this parameter, as it is still active for the multis.

Just Solarcharger ignore this limit.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·
@Pedaaa

The way I understand "not active" is that I cannot select it because is "greyed out".

0 Likes 0 ·
pedaaa avatar image pedaaa marekp commented ·

but that is just wording and interpretation.

But i agree somehow. Victron should better explain this detail in the manuals.

As reading through the forums, many many many users don´t understand how this works.

But it is simple indeed:

if DC-feed-in is ON:

MPPT Solarcharger won´t listen to CCL

it will charge with full power, only limited by CVL+0,4V.


Multiplus is limited by CCL and CVL

(so also AC-coupled PV-inverters are limited by this as well)


if DC-feed-in is OFF:

MPPT Solarcharger as well as Multis are limited by CCL and CVL

3 Likes 3 ·
marekp avatar image marekp pedaaa commented ·

@Pedaaa When one writes the manual the "wording" is everything. There should nothing be left to "interpretation".

It is simple indeed and it should be explained in such a way that there is no room for interpretation.

Exactly like You did it.


0 Likes 0 ·
nickdb avatar image nickdb ♦♦ marekp commented ·
I don't recall victron ever using "active" with that definition, so that would appear to be a misinterpretation on your part.

Even "active SOC" refers to a limit that is currently in use.

Also remember, the moment you disable feed-in, this limit would become active again.

I think you're confusing it with "available" or "configurable".

All just semantics.


1 Like 1 ·
marekp avatar image marekp nickdb ♦♦ commented ·
@nickdb If there is a room for misinerpretation that means manual is not well written.
0 Likes 0 ·
marekp avatar image marekp nickdb ♦♦ commented ·

@nickdb

@Pedaaa

Also it would be nice if this manual showed the current view of the ESS assistant.

It shows it like this:

screen-shot-2023-05-21-at-24032-pm.png

When in reality it is now this:

ess.jpg

and

screen-shot-2023-05-21-at-25220-pm.png

0 Likes 0 ·
markess avatar image
markess answered ·

Yes the Limit Charge Current setting for me just affects the power into the battery coming from the solar inverter through the Victron. The MPPT direct charging the battery is not affected.

So it seems you can't easily fully prioritise export with ESS if you have an MPPT (sometimes required in UK as we currently have some competitive export tarrifs), although I guess this is not really an ESS use case. Solved with Node-RED though.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

baxter avatar image
baxter answered ·

Maybe the wording in the DVCC manual is not misleading for you


"6) DVCC charge current limits are not applied to DC MPPTs when ESS is enabled with Allow DC MPPT to export. This is to get maximum output from the solar panels for export."


https://www.victronenergy.com/media/pg/CCGX/en/dvcc---distributed-voltage-and-current-control.html

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markess avatar image markess commented ·
Yes it is a bit odd wording. If you want max export then you don't want PV going to battery. Shame the current limit is not system wide. I use Node-RED to set battery current=0 if I want to idle the battery.
0 Likes 0 ·