question

newgen avatar image
newgen asked

RCD is NOT triggered

fi-setup.png

Hi,

I have the described test setup in a house (non-mobile, no AC in, single phase). The test button at the RCD works. However, when I make a link at the socket between PE and N, the RCD does not trip. Is this, because it is an IT circuit rather than an TT one?


Furthermore, when the 16 amp fuse is disabled, the socket measures 4 volt (depending on the distance to the multiplus inverter. Is this due to induction? Can this be the problem?


Any help would be appreciated.


Multiplus-II
fi-setup.png (30.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

It's only one socket without any loads connected to the circuit?

If yes, the RCD will not trip because there is no "illegal" current flow.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image
pwfarnell answered ·

In a standalone system the multiplus will connect the neutral and earth together. Linking neutral and earth at the socket without any load in the system can not result in any current flow.

From the manual

Ground relay (see appendix B)

With this relay, the neutral conductor of the AC output is grounded to the chassis when the back feed safety relays are open.

This ensures the correct operation of earth leakage circuit breakers in the output.