Hi,
I have the described test setup in a house (non-mobile, no AC in, single phase). The test button at the RCD works. However, when I make a link at the socket between PE and N, the RCD does not trip. Is this, because it is an IT circuit rather than an TT one?
Furthermore, when the 16 amp fuse is disabled, the socket measures 4 volt (depending on the distance to the multiplus inverter. Is this due to induction? Can this be the problem?
Any help would be appreciated.