Multiple Multiplus units and mulptiple Fronius units in Microgrid setup

hi, planning out some future upgrades. I have a Multiplus 2 unit in a microgrid with a Fronius today.
Im curiious if this can be doubled up . ie 2x Fronius Primo inverters and 2x Victron Multiplus 2 units ? Technically it fits in with the rules of 1:1 - ie there is only total of 8KW or solar to 2x 5000 VA Victron Units.
Diagram attached. microgrid.JPG

microgrid
microgrid.jpg (84.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
tim-hickman avatar image
tim-hickman answered ·

This looks good to me.

The Factor 1.0 rule requires the PV to be equal or less than the VA rating of the inverter charger - in your case 10000VA (Inverter Chargers) and 8000W (PV)