Dear sirs,
I am writing to report a problem with the US5000 series batteries in combination with Multiplus II 48/5000.
System installation details are as follows:
N. 1 Victron inverter model: Multiplus II 48 V 5000 VA
No. 1 MPPT Victron model: Smart Solar MPPT RS 450/100
N.2 Batteries Pylontech model: US5000
We had the following problems starting from 25.04.2023:
- during the day N. 5 inverter shutdown vith interruption of VAC OUT with no apparent reason (see state OFF of VE Bus)
- at 19:40 the inverter signals "LOW BATTERIES" but the SOC was 97% and the Maximum and minimum cell Voltage was 3,32 V
- from this moment untill 08.05.23 we have no longer shut down of the inverter but from the following day (27.04.2023) we have noticed an imbalance in the cells:
Maximum cell voltage 3.51V
Minimum cell voltage 3.35V
and SOC did not rise above 97% while before was reaching 100%
Starting from 08.05.2023 we have again many other shutdown of the inverter with VAC out interruption:
From the 08.05.2023 one of the batteries, when the system is full charged, did not light up the last green led while the other batterie have all the green leds on
The interpelled Victron distributor told me that's a Battery problem, the battery distributor tell me that there is an issue between all the Multiplus II and Pylontech US5000 and is reccomending not to use the US5000 but only the US3000C with Multipluss...
So as per evidence we are in the middle, somebody can help us?